Use the Tag
Properties dialog to view the configured alarms for a
selected tag. IWS
disables this command if there are open alarm worksheets. Before
using these dialogs, you should have already created the alarm
groups.
ALARM TYPES:
- HiHi: A Very High
alarm is present.
- Hi: A High alarm is
present.
- Lo: A Low alarm is
present.
- LoLo: A Very Low alarm
is present.
- Rate: An alarm based
on rate of change is present.
- Deviation: An alarm
based on deviation from a given set point is present. Example:
- If SetPoint = 50, Deviation + = 5, Deviation − = 5,
and Deviation Dead Band = 0.5;
- IWS
generates an alarm when the temp ≥ 55 or temp ≤ 45; and
- A return to the normal occurs when temp ≤ 54.5 or
temp ≥ 45.5.
ALARM LIMITS:
- HiHiLimit: When
creating Very High alarms in the Tag
Properties dialog, use this field to specify the limits. You
can access this field during runtime and use it during
modifications on the fly.
- HiLimit: When creating
High alarms in the Tag
Properties dialog, use this field to specify the limits. You
can access this field during runtime and use it during
modifications on the fly.
- LoLimit: When creating
Low alarms in the Tag
Properties dialog, use this field to specify the limits. You
can access this field during runtime and use it during
modifications on the fly.
- LoLoLimit: When
creating Very Low alarms in the Tag
Properties dialog, use this field to specify the limits. You
can access this field during runtime and use it during
modifications on the fly.
- DevSetpoint: Reference
point for a tag value deviation that triggers an alarm. Define the
alarm message in the Tag
Properties dialog or on an Alarm worksheet. You can access this
field during runtime.
- Dev+Limit: Limit
deviation to a value higher than the DevSetpoint in a tag value that triggers an alarm.
Define the alarm message in the Tag
Properties dialog or on an Alarm worksheet. You can access this
field during runtime.
- Dev+Limit: Limit
deviation to a value lower than the DevSetpoint in a tag value that triggers an alarm.
Define the alarm message in the Tag
Properties dialog or on an Alarm worksheet. You can access this
field during runtime.
- RateLimit: Limit of
rate variation in a tag value that triggers an alarm. Define the
alarm message in the Tag
Properties dialog or on an Alarm worksheet. You can access this
field during runtime.
Alarms for Integer and Real Type
Tags
From the
Tag
Properties dialog, specify an alarm for integer and
real-type tags as follows:
Alarms for Boolean-Type Tags
Use the Alarms-Bool
Type tab on the Tag
Properties dialog to specify alarm properties for
Boolean-type tags.
Figure 1. Alarms-Bool
Type Tab
Configure the parameters as follows:
- Alarms Enabled
checkbox: Click (check) to enable checking according to
configuration.
- Remote Ack tag
field: Type a tag to enable remote alarm acknowlegement, which
occurs when the tag values change.
- Translation
Enabled checkbox: Click (check) to enable the translation of
messages defined on the Options tab in the Project
Settings dialog. For additional information about
translations, see
Translation Tools.
Note:
IWS saves Alarm
messages with the Translation
Enabled attribute enabled in a file called Alarm.TXT located in your project's \DATABASE\ directory.
- Off checkbox:
Click (enable) to generate an alarm message always when the tag
value is zero.
- On checkbox: Click
(enable) to generate an alarm message always when the tag value is
one.
- Changed checkbox:
Click (enable) to generate an alarm message always when the tag
value changes.
- Text value pane:
Use the Off, On, and Ack
fields to configure mnemonics (for example, Closed or Open) for the
Off, On, and Ack alarm
states (Boolean tags only). During runtime, the Alarm Control
object will display this text in the Value column of the alarm message. You
can also access this text using the
tag fields.
Note: If you
do not configure a mnemonic, the Alarm Control object displays the
tag value (0 or 1) in the Value column.